Sounds like you have a voltage regulator problem, since your generator is generating a voltage output at a residual level, it is likely the field is not being excited. Start by checking the F1 (+) and F2 (-) leads and see if a DC voltage is present, typically something above 10 VDC. Start with that and we can go from there.
Mike L.
Re: Under voltage fault on 550 kva genset
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
07-10-2012 12:50 PM
Please check the Engine RPM. One Time this problem and solve problem
your problem solve then reply
Re: Under voltage fault on 550 kva genset
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
07-12-2012 10:57 PM
Pls clear more. The genset was running in 1500 rpm and there was no overload, suddently It's voltage dropped form 415V to 50V or the voltage's always 50V???
I think your AVR might get failed. Pls check as DC Voltage between F+ & F- after check all connection.