Load 200KV,PF 0.6,How to choose the alternator?

hi!

the customer's load is 200KVA, pf o.6,  Smooth start,   if I choose the standard alternator(PF 0.8), what the power of the alternator need, Tks!

Cat Dealer
tuyenpham

Re: Load 200KV,PF 0.6,How to choose the alternator?

200kVA, PF 0.6, electric power: 120 ekW

If you choose PF 0.8 alternator, it's kVA may be 150.

Pham Minh Tuyen (Mr)
Phu Thai CAT - Vietnam
Cat Dealer
wtc2008

Re: Load 200KV,PF 0.6,How to choose the alternator?

yijin,

 

The ekw of load  is 120ekw, the KVA is 200KVA.

 

The KVA and KW of alternator should be bigger than load, so the alternator should be less 200KVA @pf=0.8.

Because the alternator is standard designed for pf=0.8, so the prime mover is bigger.

 

But the alternator should be derated @ pf=0.6, the factor is 0.85, so the alternator should be oversized to 236KVA.

 

I suggest you select a standard 150kva/120kw(pf=0.8) genset and oversized the alternator to 236KVA.

 

Hope to help you.

 

wtc2008