heavy current flowing in neutral

hi

we are using a cat dg  D 3516 with a ups (1100kva) 

the problem is when there is normal load that is without no ups on dg only simple plant load there is normal neutral current of some 30-35 amp

but when we connect ups on ddg ther is 50% of line load on neutral 

can anybody help me in this regard

Contributor
arain1984

Re: heavy current flowing in neutral

you are check the load 

load is unbalance . load is dived 3phase

your problem solve then reply

Trusted Contributor
mikel

Re: heavy current flowing in neutral

You will need to provide some info to get a better answer. In general it sounds like you have some imbalance as pointed out in the other response, by listing each phase currnet and the neutral current you will liklely see the neutral current when the UPS is not connected as load imbalance.

 

When the UPS is connected you may be seeing harmonic current, you may be able to determine that if you have a good quality DMM and can get a frequency reading off the current, but likely you will need a power quality analyzer or recorder to properly display and document what you have on you system.

 

What does your voltage do when the UPS is brought on, does it rise or fall from the nominal value that it maintains when only the plant loads without the UPS are on? This could also be an indication of harmonics. Does the UPS have power correction capacitors installed? Have you investigated the UPS while it is on the utility source?

 

Again, better describe your system and the information you are getting, like measured values if you want better answers, otherwise you can only get speculation from what info you have provided so far.

 

Mike L.