10-17-2008 01:35 PM
Solved! Go to Solution.
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-21-2008 08:35 AM
Lockout requirements depend on the type of service activity being performed on the gen set. The typical minimum lockout points would include the following:
- Battery disconnect (to prevent engine from being started)
- Generator main breaker or downstream disconnect (although the gen set is usually connected to an ATS, the ATS can't be considered a LO point)
Depending on the configuration, the following additional lockout points might need to be considered:
- Heaters (likely to be fed from normal power source)
- control and or monitoring power (that control starting relay)
Hope this helps!
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-21-2008 09:47 AM
I think Tom makes a good point. If it's got power going to the gen set, it needs to be turned off and locked off. I think OHSA has some "fancy" wording for it, but that is their intent.
Florida Registered Electrical Contractor
ER0013091
Apopka, Florida
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-22-2008 12:51 PM
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-22-2008 01:30 PM
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-22-2008 01:32 PM
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-23-2008 05:09 PM
We also lockout the fuel supply and PT if there is one for the unit.
Four total as a minimum
1) Unit breaker
2) PT
3) Fuel valve
4) Battery disconnect
Also the other auxiliaries as mentioned, block heater, pan heater. Also air supply valve if there is an air start.
Electrical Technologist, Team Leader
(work for a utility)
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
11-24-2008 12:54 PM
The best way to lock a generator depend on three major factors
a) Type of maintenance needed carried out.
b) Type of starter (i.e. Is it electrical or pneumatic starter)
c) Type of start up configuration (i.e. Is it manual start/Auto local or Auto dead buss configured from remote)
When this has being achieved the following points of isolations could be done:
1. Isolate starter motor power or isolate power source to control panel and lockout.
2. Isolate start air or gas supply valve to starter motor and lockout.
3. Isolate fuel gas supply valve to engine and lockout
4. Isolate generator main power breaker at generator skid and switch room and lockout with a safety padlock
Note: Padlocks for Isolations must be secured according to the electrical safety rules governing the said generator.
Re: Generator lockout
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
01-08-2009 10:10 AM
Tech1 provides a good simple process. However, please remember that lockout is specifically defined as an action that someone without a key cannot undo. And tagout should go along with it. Energizing the battery charger and releasing the emergency stop are easy enough to undo for someone else without thinking too much about why they were de-energized and pressed to begin with.
Remember:
LOCKOUT = only the person who locked it can unlock it
TAGOUT = all others can see who locked it and why
-jc